NFPA 13 (02ed) section A.3.7.1(1)for beam and girder construction states
the beams to be "either supported on or framed into girders".  Wouldn't
the "supported on" help confirm calling a purlin building obstructed? I
have treated purlin buildings as obstructed construction in the past. 
Dewayne

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Thursday, October 18, 2007 2:07 PM
To: [email protected]
Subject: RE: purlins

Based on what? It clearly does not fall into panel construction due to
the space above the beam. They are not girders.

I am not fighting for or against, I just would like a conclusive answer.

Is there not a manufacturer or committee member there that could
enlighten us? I would think that the tests run on these storage heads
and such would have forced a definition for the manufacturers.

Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams
- FPDC
Sent: Thursday, October 18, 2007 1:59 PM
To: [email protected]
Subject: RE: purlins

Up here, it usually goes beams, purlins above (on) the beams, steel deck
on the purlins. The insulation goes in between the purlins. Is the
insulation going on the metal deck roof?If the insulation comes to the
bottom of the purlin, it will create a fairly flat ceiling and I would
consider it unobstructed. If there is no insulation, I would think it
would be considered obstructed.


At 02:51 PM 10/18/2007, you wrote:
>No, above them.  A typical warehouse.
>
>Living Water Fire Protection, LLC
>1160 McKenzie Road
>Cantonment, FL 32533
>850-937-1850
>Fax: 850-937-1852
>
>
>-----Original Message-----
>From: [EMAIL PROTECTED]
>[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams
>- FPDC
>Sent: Thursday, October 18, 2007 1:50 PM
>To: [email protected]
>Subject: Re: purlins
>
>Is there insulation between the purlins?
>
>
>At 02:45 PM 10/18/2007, you wrote:
> >Poll:
> >
> >Are typical 8" and 10" purlins spaced 4-5' apart with open space 
> >above the beams where the purlins rest considered OBstructed or 
> >Unobstructed construction?
> >
> >
> >
> >Living Water Fire Protection, LLC
> >
> >1160 McKenzie Road
> >
> >Cantonment, FL 32533
> >
> >850-937-1850
> >
> >Fax: 850-937-1852
> >
> >
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >To Unsubscribe, send an email 
> >to:[EMAIL PROTECTED]
> >(Put the word unsubscribe in the subject field)
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, Connecticut
>www.fpdc.com
>860.535.2080
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email 
>to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>To Unsubscribe, send an email 
>to:[EMAIL PROTECTED]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to