Hi Ron, Yikes, not the hose valves just the valve in the test header
LINE. Opps left that key word out. 

John 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher,
Ron
Sent: Friday, October 19, 2007 12:43 PM
To: [email protected]
Subject: RE: Fire Pump Test Header Valve Supervision

Why monitor the hose gates? Monitor the big valve inside unless it is a
wet test header without a main control valve.

Ron Fletcher
Aero Automatic
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Friday, October 19, 2007 8:13 AM
To: [email protected]
Subject: Fire Pump Test Header Valve Supervision


Does anyone have product reference for a tamper switch and or tamper
switch/valve assembly configured for use on a fire pump test header
aside from pull type (PTS) cable devices ?.

Thanks

John Drucker
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to