Gregg, Aside from from preventing the test header line and outlets from freezing (that's the obvious part up north) there is a code reference;
1999 NFPA-20 2-11 Exception: "The test outlet control valves shall be supervised closed". One could always cite 2002 NFPA-13 8.15.3.1.1 in colder climates. On the jockey pump. I see most if not all valves supervised. Is there a direct code reference ?. 1999 NFPA-20 2-19.5 could and would be cited where a jockey pump has been bypassed resulting in the main fire pump operating to maintain system pressure. I believe that because 1999 NFPA-20 2-19.3 requires indicating valves and most often those are integrated with a tamper device the valves get connected to the building fire alarm system as supervisory causing. John Drucker Fire Protection Subcode Official -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Gregg Sent: Monday, October 22, 2007 7:43 AM To: [email protected] Subject: RE: Fire Pump Test Header Valve Supervision If I may ask the obvious, where does the code state that the test header valve requires supervision? Operation of it would not impede the fire protection system. While I'm sticking my neck out, is the jockey pump control valve supposed to be supervised? Gregg -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of John Drucker Sent: Friday, October 19, 2007 6:43 PM To: [email protected] Subject: RE: Fire Pump Test Header Valve Supervision Mike, Please; [EMAIL PROTECTED] John -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of MIKE HENKE Sent: Friday, October 19, 2007 5:10 PM To: [email protected] Subject: RE: Fire Pump Test Header Valve Supervision Make sure about it monitoring the valve in the closed position. Chances are you will have to almost completely open the valve before the switches will activate. Typically the switches are set to activate within the first 2 revolutions of the handwheel or 1/5 of the valve travel from the fully open position. So if you wire it to monitor the valve closed, most likely you will have to open it to within 2 revolutions of fully open or 4/5 open before the switches will trip. Confirm this with Vic before proceeding. They may have special modifications for this situation. We have handled this in the past by mounting a bracket to the outside of the valve body and using the indicating flag to operate the standard Potter butterfly tamper switch. I can send a drawing if necessary. Regards, mike >>> "Joe Burtell" <[EMAIL PROTECTED]> 10/19/2007 12:07 PM >>> Look at the Vic 705W Butterfly valve. I just checked the datasheet. It will monitor in the fully open or closed position. Joe Burtell, SET, CFPS Burtell Fire Protection, Inc. [EMAIL PROTECTED] www.burtellfire.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mike Wisneski Sent: Friday, October 19, 2007 11:01 AM To: [email protected] Subject: RE: Fire Pump Test Header Valve Supervision John, I went through the same exercise last month. The only luck I had was with Ferguson Fire & Fab out of Tucker, GA. They have a company that will alter a butterfly tamper to work correctly with a fire pump test header. Contact Jim Sutton. Mike Wisneski -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of John Drucker Sent: Friday, October 19, 2007 11:13 AM To: [email protected] Subject: Fire Pump Test Header Valve Supervision Does anyone have product reference for a tamper switch and or tamper switch/valve assembly configured for use on a fire pump test header aside from pull type (PTS) cable devices ?. Thanks John Drucker _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) -- No virus found in this incoming message. Checked by AVG Free Edition. Version: 7.5.488 / Virus Database: 269.15.1/1079 - Release Date: 10/19/2007 5:10 AM _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)