IF FM GLOBAL IS THE AHJ, JUST CALL THE GUY AND ASK HIM/ HER. I ASSUME  YOU'RE 
RUNNING UP AGAINST A CASE OF A MECHANICAL CONTRACTOR INSTALLING UG PIPE  ON A 
POWER PLANT.
 
FOREST
CHEROKEE FIRE

I agree  this seem to be an odd way of testing underground. I would recommend 
that you  check with the manufacture of the pipe before you apply compressed 
gas N2 or  air. The issue with more brittle plastics is the danger form flying 
shrapnel.  As a general rule plastic and compressed gas is a bad idea. (PEX 
is the  exception)


Mike Cabral

---- Timothy W Goins  <[EMAIL PROTECTED]> wrote: 
> How would you measure the acceptable  loss? How would know if the loss was
> from a fitting, a joint, a hole,  or a valve? How would you see the leak if
> there was a small one? Why  would you want to test this way?
> 
> -----Original  Message-----
> From: [EMAIL PROTECTED]
>  [mailto:[EMAIL PROTECTED] On Behalf Of Loren  
Johnson
> Sent: Thursday, October 11, 2007 11:23 AM
> To:  Sprinkler Forum
> Subject: UNDERGGROUND FIRE MAIN TESTING
>  
> 
> Forum:
> 
> We have a situation that just came  up.....here's the
> quick question side of things:
> 
> Can  listed plastic underground fire main piping be
> tested with nitrogen  instead of the typical
> hydro-static water method?  I've always  been told this
> is not acceptable, and there are no sections on  the
> test form that indicate this to be an option. In
>  addi-tion, since FM Global is the insuance carrier for
> this project,  there is a very strong possibility the installation would be
>  unacceptable when field
> in-spected.      
>  
> Thanks in advance.
> 
> 
> Loren Johnson
>  Peoria, IL 
> 
> 
>  
>  
____________________________________________________________________________
>  ________
> Check out the hottest 2008 models today at Yahoo!  Autos.
> http://autos.yahoo.com/new_cars.html
>  _______________________________________________
> Sprinklerforum mailing  list
> [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>  
> To Unsubscribe, send an email  to:[EMAIL PROTECTED]
> (Put the word unsubscribe  in the subject field)
> 
> 
>  _______________________________________________
> Sprinklerforum mailing  list
> [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>  
> To Unsubscribe, send an email  to:[EMAIL PROTECTED]
> (Put the word unsubscribe  in the subject  field)
_______________________________________________
Sprinklerforum  mailing  list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To  Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put  the word unsubscribe in the subject field)







************************************** See what's new at http://www.aol.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to