If the area is filled with Insul it does not require sprinkler protection per 13, so per the attached from Blazemaster you can use CPVC.

"CPVC pipe and fittings are not intended to be installed in combustible concealed spaces where sprinklers are required by ANSI/NFPA 13, 13R, or 13D as applicable."

"CPVC pipe and fittings are intended for use in areas where the maximum ambient temperature does not exceed 150°F. If the ambient temperature is expected to exceed this limitation, refer to the manufacturer's installation instructions for additional information on methods to reduce the pipe exposure temperatures. These pipe and fittings are not intended to be installed in outdoor applications."

This would be similar to installing CPVC in a flat roof made of TJI's, and filled with Insul.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "Bob Knight" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, October 23, 2007 2:48 PM
Subject: CPVC in Combustible Space with Insulation


I have a situation with a "stair tower" that requires two sprinklers at the
top level. This is a 13 project using CPVC in most places. My question is,
can I use CPVC at the top of this stair tower which is combustible
construction (trusses) but is filled completely w/ noncombustible
insulation? I have searched the CPVC data and I don't think that I can, but
it would be easier then transitioning to steel.

Thank you,

Bob Knight, CET
(208) 495-2057
[EMAIL PROTECTED]
www.firebyknight.com


No virus found in this outgoing message.
Checked by AVG Free Edition.
Version: 7.5.488 / Virus Database: 269.15.5/1085 - Release Date: 10/22/2007
10:35 AM


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to