Been there done that and all that!  This one is small with no way anybody
will ever crawl it let alone access it, not even Larry.  

BK

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Tuesday, October 23, 2007 5:12 PM
To: [email protected]
Subject: RE: CPVC in Combustible Space with Insulation

So long as you've analyzed it, and are comfortable with it, and in this one,
if no one is crawling around out there unless they're shorter than red, then
go for it. We'd tented for years, but after a couple lions got us while
camping out, we stay inside.

We've done everything but put the insulation in for some guys and they still
screw it up- not to mention when Larry the cable guy comes thru in a couple
years with the newest cable type for some new Comm7R protocol and steps on
my pipe.

I don't care who ya are, that there pipe is busted.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bob Knight
Sent: Tuesday, October 23, 2007 7:06 PM
To: [email protected]
Subject: RE: CPVC in Combustible Space with Insulation

Scott and George,
Around these here parts we commonly "tent" the insulation.  This is a very
standard practice within the local industry and has shown itself to be very
effective over many years.  The only draw back is when someone collapses the
pocket and the insulation can then fill in around the piping.  In this
instance the "attic" space in question is very shallow with no room to move
around in it.  There should be no difficulties with this one.

Thanks,
Bob

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Scott A.
Futrell
Sent: Tuesday, October 23, 2007 4:57 PM
To: [email protected]
Subject: RE: CPVC in Combustible Space with Insulation

Where is the project located?  If you put the CPVC in the insulation, above
the ceiling, it will freeze.

Scott   

(763) 425-1001 Office 
(612) 759-5556 Cell 



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bob Knight
Sent: Tuesday, October 23, 2007 4:04 PM
To: [email protected]
Subject: RE: CPVC in Combustible Space with Insulation

Thanks Thom,
That verifies what Steve was saying.

Thanks again,
Bob

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Tuesday, October 23, 2007 2:58 PM
To: [email protected]
Subject: Re: CPVC in Combustible Space with Insulation

If the area is filled with Insul it does not require sprinkler protection 
per 13, so per the attached from Blazemaster you can use CPVC.

"CPVC pipe and fittings are not intended to be installed in combustible 
concealed spaces where sprinklers are required by ANSI/NFPA 13, 13R, or 13D 
as applicable."

"CPVC pipe and fittings are intended for use in areas where the maximum 
ambient temperature does not exceed 150°F. If the ambient temperature is 
expected to exceed this limitation, refer to the manufacturer's installation

instructions for additional information on methods to reduce the pipe 
exposure temperatures. These pipe and fittings are not intended to be 
installed in outdoor applications."

This would be similar to installing CPVC in a flat roof made of TJI's, and 
filled with Insul.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- 
From: "Bob Knight" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, October 23, 2007 2:48 PM
Subject: CPVC in Combustible Space with Insulation


>I have a situation with a "stair tower" that requires two sprinklers at the
> top level.  This is a 13 project using CPVC in most places.  My question 
> is,
> can I use CPVC at the top of this stair tower which is combustible
> construction (trusses) but is filled completely w/ noncombustible
> insulation?  I have searched the CPVC data and I don't think that I can, 
> but
> it would be easier then transitioning to steel.
>
> Thank you,
>
> Bob Knight, CET
> (208) 495-2057
> [EMAIL PROTECTED]
> www.firebyknight.com
>
>
> No virus found in this outgoing message.
> Checked by AVG Free Edition.
> Version: 7.5.488 / Virus Database: 269.15.5/1085 - Release Date: 
> 10/22/2007
> 10:35 AM
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG Free Edition. 
Version: 7.5.488 / Virus Database: 269.15.5/1085 - Release Date: 10/22/2007
10:35 AM
 

No virus found in this outgoing message.
Checked by AVG Free Edition. 
Version: 7.5.488 / Virus Database: 269.15.5/1085 - Release Date: 10/22/2007
10:35 AM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG Free Edition. 
Version: 7.5.488 / Virus Database: 269.15.5/1085 - Release Date: 10/22/2007
10:35 AM
 

No virus found in this outgoing message.
Checked by AVG Free Edition. 
Version: 7.5.488 / Virus Database: 269.15.5/1085 - Release Date: 10/22/2007
10:35 AM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

No virus found in this incoming message.
Checked by AVG Free Edition. 
Version: 7.5.488 / Virus Database: 269.15.5/1085 - Release Date: 10/22/2007
10:35 AM
 

No virus found in this outgoing message.
Checked by AVG Free Edition. 
Version: 7.5.488 / Virus Database: 269.15.5/1085 - Release Date: 10/22/2007
10:35 AM
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to