Something new to me popped up today as we are now using the 2002 editions of
13 & 72 here.

On a dry pipe sprinkler the National Fire Alarm Code - NFPA 72 states that
the air supervisory sensor shall signal on loss of 10 PSI but also on 10 PSI
greater than the system set pressure.  Check out 5.13 for yourself but I'm
thinking Ive never seen or tested for air greater than 10 PSI of the set
pressure before.

How is this being handled in the field during installs and maintenance ?
Does the typical air pressure switch in the little red cover actually cover
both loss and increase pressures?

Thanks.

Dave - a NJ AHJ