Something new to me popped up today as we are now using the 2002 editions of 13 & 72 here.
On a dry pipe sprinkler the National Fire Alarm Code - NFPA 72 states that the air supervisory sensor shall signal on loss of 10 PSI but also on 10 PSI greater than the system set pressure. Check out 5.13 for yourself but I'm thinking Ive never seen or tested for air greater than 10 PSI of the set pressure before. How is this being handled in the field during installs and maintenance ? Does the typical air pressure switch in the little red cover actually cover both loss and increase pressures? Thanks. Dave - a NJ AHJ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)