If the "little red box" is a Potter PS40-2A is has 2 sets of contacts
in it. One for "Low Air" and the other for "High Air". It is factory
set to operate on Increase at 50 PSI and on Decrease at 30 PSI. The
set pressure can be adjusted from 10-175 PSI. The 2 switches can be
adjusted  independently of each other to anywhere in that range.

If the "little red box" is a Potter PS40-1A it only has 1 set of
contacts that operates on decrease. If is factory set to operate on
decrease at 30 PSI.

I would think the newer System Sensor brand can do the about the same.

I have found that most of the time the alarm company does not tie into
the high pressure switch.




Tuesday, October 23, 2007, 5:52:35 PM, you wrote:

> Something new to me popped up today as we are now using the 2002 editions of
> 13 & 72 here.

> On a dry pipe sprinkler the National Fire Alarm Code - NFPA 72 states that
> the air supervisory sensor shall signal on loss of 10 PSI but also on 10 PSI
> greater than the system set pressure.  Check out 5.13 for yourself but I'm
> thinking Ive never seen or tested for air greater than 10 PSI of the set
> pressure before.

> How is this being handled in the field during installs and maintenance ?
> Does the typical air pressure switch in the little red cover actually cover
> both loss and increase pressures?

> Thanks.

> Dave - a NJ AHJ

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)


-- 
Best regards,
 Charles                            mailto:[EMAIL PROTECTED]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to