Well, I've been deemed incompetent to sign off on a 20 head 13D system here
in PA, need to run it past a Registered Design professional according to the
3rd party. He's right, per our PA UCC, just applied real world logic for a
moment and was a little frustrated by the irony of it all. Maybe I'll send
it to a Professional Land Surveyor for a letter stating "generally conforms
to the building" which is all our UCC requires the RDP to say. 

Being a 13D, he could comment that we've used an unlisted pump, unlisted
tank, in accordance with 13D.

So maybe we'll hang our 1" CPVC as you describe, by the tie its all over.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Charles
Thurston
Sent: Tuesday, October 30, 2007 12:44 PM
To: George Church
Subject: Re[2]: hanger specs

Hello George,

As I read this I got a mental image of 1" pipe hung with 1" rod on a
clevis hanger.  Ha Ha

Tuesday, October 30, 2007, 12:18:13 PM, you wrote:

> They're going to list bigger rod than you ever imagined, hanger spacing
that
> would put you out of business if you didn't include it, and if you give
them
> an order of magnitude on the added cost, you'll likely get an addendum
that
> allows NFPA #13 requirements be met and have a nice day. Did I mention
> Clevis?

> glc

> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of G. Tim
Stone
> Sent: Tuesday, October 30, 2007 10:08 AM
> To: [email protected]
> Subject: RE: hanger specs

> Greg,

>  

> I googled and received this information back: 

>  

> MSS SP-58 Pipe Hangers and Supports - Materials, Design and Manufacture

>  

>  

> G. Tim Stone

>  

>  

> NICET Level III Engineering Technician

> Fire Protection Sprinkler Design

> and Consulting Services

>  

> 117 Old Stage Rd. - Essex Jct., VT. 05452

> TEL: (802) 434-2968          Fax: (802) 434-4343

>                 [EMAIL PROTECTED]

>  

>  

>> -----Original Message-----

>> From: [EMAIL PROTECTED] [mailto:sprinklerforum-

>> [EMAIL PROTECTED] On Behalf Of Greg McGahan

>> Sent: Tuesday, October 30, 2007 9:59 AM

>> To: [email protected]

>> Subject: hanger specs

>> 

>> We are looking at an airport job with these hanger specs and I am not

>> familiar with MSS-SP-58. Does anyone know what these are?

>> 

>> Thanks,

>> 

>> Greg

>> 

>> 

>> 

>> Living Water Fire Protection, LLC

>> 

>> 1160 McKenzie Road

>> 

>> Cantonment, FL 32533

>> 

>> 850-937-1850

>> 

>> Fax: 850-937-1852

>> 

>> 

>> 

>> _______________________________________________

>> Sprinklerforum mailing list

>> [email protected]

>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

>> 

>> To Unsubscribe, send an email to:[EMAIL PROTECTED]

>> (Put the word unsubscribe in the subject field)

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)


-- 
Best regards,
 Charles                            mailto:[EMAIL PROTECTED]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to