Must use sprinkler that is listed and tested for this specific use to provide a 
2 hour fire rating.  Suggest exploring ICC Legacy testing and evaluation of 
products.



Rahe Loftin



----- Original Message -----
From: "Karen Purvis" [EMAIL PROTECTED]
Sent: 10/31/2007 12:59 PM AST
To: [email protected]
Subject: Need Help fast



I need to know if there is a code anywhere that states you can or can not
use a standard pendant head as a window wash. I have a glass wall that I
need to be fire rated and I have a contractor telling me by code he can use
a pendant head instead of a deluge head or a Tyco window sprinkler. The only
code I see that possibly address this is 21.20.1.2.1 and it only says you
have to use automatic heads. Any help!!!!!

Karen Purvis