Must use sprinkler that is listed and tested for this specific use to provide a 2 hour fire rating. Suggest exploring ICC Legacy testing and evaluation of products.
Rahe Loftin ----- Original Message ----- From: "Karen Purvis" [EMAIL PROTECTED] Sent: 10/31/2007 12:59 PM AST To: [email protected] Subject: Need Help fast I need to know if there is a code anywhere that states you can or can not use a standard pendant head as a window wash. I have a glass wall that I need to be fire rated and I have a contractor telling me by code he can use a pendant head instead of a deluge head or a Tyco window sprinkler. The only code I see that possibly address this is 21.20.1.2.1 and it only says you have to use automatic heads. Any help!!!!! Karen Purvis Designer Facility Systems Consultants 714 S Gay St Knoxville, TN 37902 ph.865-246-0164 fax 865-246-1084 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)