Probably a separate issue, since you indicate that you have a glass wall
that is required to be rated, but if you are in the wide world of IBC
land, as George C. points out (beat me to the punch), you may want to
note IBC section 404.5 (2003 ed.), which addresses specifically the
separation of atriums.
404.5 Enclosure of atriums. Atrium spaces shall be separated
from adjacent spaces by a 1-hour fire barrier wall.
Exceptions:

1. A glass wall forming a smoke partition where automatic
sprinklers are spaced 6 feet (1829 mm) or less
along both sides of the separationwall, or on the room
side only if there is not a walkway on the atrium side,
and between 4 inches and 12 inches (102mmand 305
mm) away from the glass and so designed that the entire
surface of the glass is wet upon activation of the
sprinkler system. The glass shall be installed in a
gasketed frame so that the framing system deflects
without breaking (loading) the glass before the sprinkler
system operates.


=-=-=-=-=-=-=-=-=-=-=-=-=-=-=-=
Eric G. Longman
Fire Protection Design & Analysis
 
AREVA NP Inc.
An AREVA and Siemens Company
6100 Southwest Boulevard, Suite 400
Fort Worth, Texas 76109
(817) 737-1170 - Office
(817) 737-1100 - Fax
 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Mark
Hasenmyer
Sent: Wednesday, October 31, 2007 12:22 PM
To: [email protected]
Subject: RE: Need Help fast

I have seen a water curtain (closely space standard sprinklers)
installed on
both sides of a glass wall that required fire rating, i.e. corridor
wall.  I
haven't looked up the code reference for this since I haven't had to
convince someone to accept the idea; I've only seen it in the field on
occasion.

Mark Hasenmyer, PE
MEH Fire Protection Engineering LLC
1311 River Oaks Drive
Flower Mound, TX 75028
Office (972) 874-2662
Fax (972) 874-5591


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Karen
Purvis
Sent: Wednesday, October 31, 2007 12:00 PM
To: [email protected]
Subject: Need Help fast

I need to know if there is a code anywhere that states you can or can
not
use a standard pendant head as a window wash. I have a glass wall that I
need to be fire rated and I have a contractor telling me by code he can
use
a pendant head instead of a deluge head or a Tyco window sprinkler. The
only
code I see that possibly address this is 21.20.1.2.1 and it only says
you
have to use automatic heads. Any help!!!!!

Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to