Probably a separate issue, since you indicate that you have a glass wall that is required to be rated, but if you are in the wide world of IBC land, as George C. points out (beat me to the punch), you may want to note IBC section 404.5 (2003 ed.), which addresses specifically the separation of atriums. 404.5 Enclosure of atriums. Atrium spaces shall be separated from adjacent spaces by a 1-hour fire barrier wall. Exceptions:
1. A glass wall forming a smoke partition where automatic sprinklers are spaced 6 feet (1829 mm) or less along both sides of the separationwall, or on the room side only if there is not a walkway on the atrium side, and between 4 inches and 12 inches (102mmand 305 mm) away from the glass and so designed that the entire surface of the glass is wet upon activation of the sprinkler system. The glass shall be installed in a gasketed frame so that the framing system deflects without breaking (loading) the glass before the sprinkler system operates. =-=-=-=-=-=-=-=-=-=-=-=-=-=-=-= Eric G. Longman Fire Protection Design & Analysis AREVA NP Inc. An AREVA and Siemens Company 6100 Southwest Boulevard, Suite 400 Fort Worth, Texas 76109 (817) 737-1170 - Office (817) 737-1100 - Fax -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mark Hasenmyer Sent: Wednesday, October 31, 2007 12:22 PM To: [email protected] Subject: RE: Need Help fast I have seen a water curtain (closely space standard sprinklers) installed on both sides of a glass wall that required fire rating, i.e. corridor wall. I haven't looked up the code reference for this since I haven't had to convince someone to accept the idea; I've only seen it in the field on occasion. Mark Hasenmyer, PE MEH Fire Protection Engineering LLC 1311 River Oaks Drive Flower Mound, TX 75028 Office (972) 874-2662 Fax (972) 874-5591 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Karen Purvis Sent: Wednesday, October 31, 2007 12:00 PM To: [email protected] Subject: Need Help fast I need to know if there is a code anywhere that states you can or can not use a standard pendant head as a window wash. I have a glass wall that I need to be fire rated and I have a contractor telling me by code he can use a pendant head instead of a deluge head or a Tyco window sprinkler. The only code I see that possibly address this is 21.20.1.2.1 and it only says you have to use automatic heads. Any help!!!!! Karen Purvis Designer Facility Systems Consultants 714 S Gay St Knoxville, TN 37902 ph.865-246-0164 fax 865-246-1084 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)