Steve,

Idle thought/question? Would IBC consider extending the OH fifteen
feet into the LH to be equivalent to a fire rated curtain or water
curtain?

On Nov 13, 2007 9:52 AM, Steve Leyton <[EMAIL PROTECTED]> wrote:
> Okay, seriously.
>
> A platform is a raised surface, that may be slab-on-grade, or framed up from 
> a structural floor assembly.   Generally, the ceiling over it is the same one 
> that is above the seating/assembly areas of the larger room in which the 
> platform is located.
>
> A stage has a proscenium that separates the back of house space from the 
> seating/assembly space.  Also generally, it has no suspended ceiling or a 
> much higher ceiling over it, known in the theater biz as "bag and flag" 
> space.  Curtains, lighting, set pieces, etc., etc. are potentially 
> stored/suspended in this space and it creates a unique and elevated fire 
> load.  Hence, stages are protected for Ordinary Hazard and assembly areas 
> (and platforms) for Light.   There is also a requirement that either the 
> stage curtain be fire-rated, or that a "fire-curtain" assembly be provided, 
> or that a water curtain or deluge system be provided at the proscenium to 
> protect the separation between a legitimate "stage" and the A-group.
>
> Steve Leyton
> Protection Design & Consulting
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Randy Knutson
> Sent: Thursday, November 08, 2007 5:28 PM
> To: [email protected]
> Subject: All the worlds a stage
>
> Forum Members,
>
>
>
> What's the difference between a platform and a stage? I'm looking at a
> charter school auditorium/gym. The stage is a platform elevated 1'-6" above
> the concrete slab. There is ACT ceiling at 20 ft and a 12ft x 40ft opening
> to the auditorium. There doesn't appear to be room for drop scenery like in
> a professional theatre stage.
>
>
>
> Class III standpipes and OH group II seem excessive for this application. I
> fear what might happen if a 90 lb drama student decides to mess with 1½"
> fire hose with 100psi raging behind it.
>
>
>
> I've found some info in NFPA 101 but I still confused on the stage and
> platform definitions.
>
>
>
> Any help will be greatly appreciated
>
> Thanks,
>
>
>
> Randy Knutson
>
> Shilo Automatic Sprinkler, Inc.
>
>
>
> P.S.
>
>
>
> Bob I'm not ignoring you.
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to