Subject: NFPA 13R Garages
According to the automatic sprinkler systems handbook 2002 NFPA 13R 6.7.2.1 for areas outside the dwelling unit the NFPA13 apply as far as design discharge, number of design sprinklers, sprinkler coverage, position of sprinklers. According to section 6.7.3 garages design criteria for garages accessible by people from more than one dwelling unit shall be covered as per 6.7.2. Further A.6.7.3.3 points out that a common mistake the application of the location (eg combustible spaces) from NFPA 13, but the location requirements described in NFPA 13R 6.8. Since 6.8.5 allow the omission of heads in attics. So the intention of NFPA 13R not to require heads in attics or combustible spaces above residential garages? If anybody dealt with this before please advise. Peter Nadhazy Marathon Fire Protection, Inc. 578 Arcade Avenue Seekonk, MA 02771 (508)336-4300 (508)336-4232 [EMAIL PROTECTED] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)