Scott,
I don't know about reconciled, however I would think that the provisions
of section 1.5 (equivalency) and 1.6 (new technologies) would make the
special listing an acceptable method of protection. I guess the
difference might be that using the specific listed attic sprinklers you
have to calculate only five flowing heads, and if the design included
only standard spray sprinklers it must include seven flowing sprinklers.
At least that would be my read on it.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
å... .... wrote:
2002 and 2007 NFPA 13 requires calculating 7 sprinklers along a line
(11.2.3.4.2 in 2002)
A manufacturer special listing for attic sprinkler requires 5 sprinklers
along a line
in cases without a hip roof.
How is that reconciled?
scot deal