OK.

it was curious for me to understand how the special
listing sprinkler not only got to name the sprinkler coverage
area, but seemed to name its remote area, too.

maybe they fall under the quick-response sprinklers
with extended coverage per 2007 NFPA 13, Section
11.2.3.2.3.2 where the minimum number of sprinklers
calculated must be 5.

thanks,

Scot Deal
excelsior fire

********************

I don't know about reconciled, however I would think that the provisions
of section 1.5 (equivalency) and 1.6 (new technologies) would make the
special listing an acceptable method of protection.  I guess the
difference might be that using the specific listed attic sprinklers you
have to calculate only five flowing heads, and if the design included
only standard spray sprinklers it must include seven flowing sprinklers.