OK. it was curious for me to understand how the special listing sprinkler not only got to name the sprinkler coverage area, but seemed to name its remote area, too.
maybe they fall under the quick-response sprinklers with extended coverage per 2007 NFPA 13, Section 11.2.3.2.3.2 where the minimum number of sprinklers calculated must be 5. thanks, Scot Deal excelsior fire ******************** I don't know about reconciled, however I would think that the provisions of section 1.5 (equivalency) and 1.6 (new technologies) would make the special listing an acceptable method of protection. I guess the difference might be that using the specific listed attic sprinklers you have to calculate only five flowing heads, and if the design included only standard spray sprinklers it must include seven flowing sprinklers. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)