With one except, you are absolutely correct that they are two different types of sprinklers with two different design criteria. How would one mix the assignment of the size of a remote area within one compartment? So if it is done twice, does a double negative make it a positive????

The exception is that mechanical closets can use a QR SPRAY sprinkler and I would also argue the IBC required balcony is enough of a separate area to treat independently.

Roland

On Dec 12, 2007, at 2:29 PM, Dewayne Martinez wrote:

NFPA 13R 07 ed
I see that 6.7.7.1.3 allows us to use QR sprinklers in a dwelling unit
as long as there is no more that 4 QR sprinklers in the compartment and
we calc the compartment at a 0.1 over the entire compartment.
We have been asked to design a building typical to the way another
contractor did it by installing a QR dry pnd off the dry system and RES hsw in the same compartment. I was always under the impression that you
could not mix the two types in the same compartment.  Am I wrong?
Thanks,
Dewayne