Just to clarify. You are permitted to use QR only when the total number of sprinklers in the DWELLING UNIT does not exceed four. If the DWELLING UNIT contains five sprinklers or more, then you are forced to use residential sprinklers. Scott Mitchell
Dewayne Martinez <[EMAIL PROTECTED]> wrote: NFPA 13R 07 ed I see that 6.7.7.1.3 allows us to use QR sprinklers in a dwelling unit as long as there is no more that 4 QR sprinklers in the compartment and we calc the compartment at a 0.1 over the entire compartment. We have been asked to design a building typical to the way another contractor did it by installing a QR dry pnd off the dry system and RES hsw in the same compartment. I was always under the impression that you could not mix the two types in the same compartment. Am I wrong? Thanks, Dewayne _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) --------------------------------- Never miss a thing. Make Yahoo your homepage. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)