Any jurisdiction that has adopted the IBC will have that authority via 2006
IBC 901.4, 2006 IFC 903.3.6, and 2003 NFPA-14 4.8.2.2 which specifically
provides; "where a fire department uses fittings that differ from those
specified (2 1/2" Threaded per 4.8.2), fittings compatible with local fire
department equipment SHALL be used and their minimum size shall be 65mm
(2-1/2)""

Keep in mind that "approval" is that which is acceptable to the authority
having jurisdiction (2003 NFPA-14.3.2.1) In all cases a fire department
connection is the sole jurisdiction of the fire department.

If you feel the need to document the requirement explain and ask the local
AHJ to correspond accordingly for your file.  I have a jurisdiction that
requires 5" LDH FDC's and we stipulate this in writing to the designer and
or contractor.

Lastly if the code requires coordination of fire department threads and
fittings (which it does) non-compliance will only result in the system not
receiving approval and occupancy being delayed. Remember the fire department
is the end user of FDC's and Hose Valves.

Sincerely,
John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey

Safe Buildings Save Lives



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of scott
mitchell
Sent: Saturday, December 22, 2007 9:39 PM
To: [email protected]
Subject: RE: Storz Connections

I would push for the AHJ to provide documentation of the requirement (either
local policy or ordinance) to use Storz on the FDCs in that jurisdiction. If
he's just making a "request", then you aren't "required" to do it and
shouldn't since none are listed. If push comes to shove, then get a FPE to
evaluate and sign off on the arrangement.
   
  Scott Mitchell

[EMAIL PROTECTED] wrote:
  That's understood. But when the Fire Marshal is the AHJ and requests those
be installed so their fire trucks can connect to your system, are you going
to tell him no because it's not a listed component?


       
---------------------------------
Never miss a thing.   Make Yahoo your homepage.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)