Any jurisdiction that has adopted the IBC will have that authority via 2006 IBC 901.4, 2006 IFC 903.3.6, and 2003 NFPA-14 4.8.2.2 which specifically provides; "where a fire department uses fittings that differ from those specified (2 1/2" Threaded per 4.8.2), fittings compatible with local fire department equipment SHALL be used and their minimum size shall be 65mm (2-1/2)""
Keep in mind that "approval" is that which is acceptable to the authority having jurisdiction (2003 NFPA-14.3.2.1) In all cases a fire department connection is the sole jurisdiction of the fire department. If you feel the need to document the requirement explain and ask the local AHJ to correspond accordingly for your file. I have a jurisdiction that requires 5" LDH FDC's and we stipulate this in writing to the designer and or contractor. Lastly if the code requires coordination of fire department threads and fittings (which it does) non-compliance will only result in the system not receiving approval and occupancy being delayed. Remember the fire department is the end user of FDC's and Hose Valves. Sincerely, John Drucker Fire Protection Subcode Official (AHJ) New Jersey Safe Buildings Save Lives -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of scott mitchell Sent: Saturday, December 22, 2007 9:39 PM To: [email protected] Subject: RE: Storz Connections I would push for the AHJ to provide documentation of the requirement (either local policy or ordinance) to use Storz on the FDCs in that jurisdiction. If he's just making a "request", then you aren't "required" to do it and shouldn't since none are listed. If push comes to shove, then get a FPE to evaluate and sign off on the arrangement. Scott Mitchell [EMAIL PROTECTED] wrote: That's understood. But when the Fire Marshal is the AHJ and requests those be installed so their fire trucks can connect to your system, are you going to tell him no because it's not a listed component? --------------------------------- Never miss a thing. Make Yahoo your homepage. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)