I just finished pre-testing and AHJ testing a high-rise hotel (22 flrs.) and
the contractor used the new field adjustable prv's for the hose valves and
sprinkler floor controls.
I was wondering how many members here have had a chance to install them yet.
I'm not going to shill these valves but they sure are a lot easier to
install and adjust over the other ones we've been testing for years.  The
1/4" tappings make it a snap to install a system-side gauge over a
mechanical tee.
One issue I did have was their modulation action.  Mostly on the straight
pattern valves that were used for sprinkler pressure reduction, we found the
valves to close down slightly and then open back up the flow.  We initially
set the floor control valves at 200 GPM and then throttled down to 50 GPM to
verify even pressure modulation and they worked fine but when we would have
them back to flowing 200, they would slow down the flow themselves to about
150 and then back to 200 all by themselves, weird.  This was on the
residential floors only.  On the non-residential floors, we set them at
300-500, depending on the contractor's design and had no problems.
I was just wondering if any if you had used and set these and had any
similar circumstances.
Merry Christmas Campers,
Tom Duross