We had Tyco run a test for NFPA 13 with residential sidewall installed above
cabinets mounted a 1' or so below. It was a fire on the counter top and the
cabinets were wrapped in craft paper to measure the water droplet wetting.
The test failed, the cabinets shielded the fire. The sprinklers was not able
to extinguish the fire, it burnt out when the fuel ran out. Your situations
is a little different but it's food for thought. I have the test on video,
you might be able to get them to send you a copy if you want.

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
www.burtellfire.com

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- FPDC
Sent: Wednesday, December 26, 2007 8:21 AM
To: [email protected]
Subject: res sidewall obstruction

I am working on a project where an old school is being converted to 
Condos. The ceilings in the units are approximately 12 ft. The 
original design called for sidewall sprinklers at about 11'-7". The 
owner has now added closets that stick out into the room approx 
2'-6". The top of the closets are approx 8'-6". Do these closets now 
create an obstruction? The requirements of 8.10.7.2.2 are met, but 
the diagram only shows a wall.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to