Todd, IMHO,I think you are ok as long as the sprinkler is not located directly above the closet, see 8.10.7.1.5.3. Otherwise, since it is located more than 18" below the deflector, you would follow section 8.10.7.3. Dewayne
-----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Joe Burtell Sent: Wednesday, December 26, 2007 9:45 AM To: [email protected] Subject: RE: res sidewall obstruction We had Tyco run a test for NFPA 13 with residential sidewall installed above cabinets mounted a 1' or so below. It was a fire on the counter top and the cabinets were wrapped in craft paper to measure the water droplet wetting. The test failed, the cabinets shielded the fire. The sprinklers was not able to extinguish the fire, it burnt out when the fuel ran out. Your situations is a little different but it's food for thought. I have the test on video, you might be able to get them to send you a copy if you want. Joe Burtell, SET, CFPS Burtell Fire Protection, Inc. [EMAIL PROTECTED] www.burtellfire.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - FPDC Sent: Wednesday, December 26, 2007 8:21 AM To: [email protected] Subject: res sidewall obstruction I am working on a project where an old school is being converted to Condos. The ceilings in the units are approximately 12 ft. The original design called for sidewall sprinklers at about 11'-7". The owner has now added closets that stick out into the room approx 2'-6". The top of the closets are approx 8'-6". Do these closets now create an obstruction? The requirements of 8.10.7.2.2 are met, but the diagram only shows a wall. Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)