Todd,
IMHO,I think you are ok as long as the sprinkler is not located directly
above the closet, see 8.10.7.1.5.3.  Otherwise, since it is located more
than 18" below the deflector, you would follow section 8.10.7.3.
Dewayne 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe
Burtell
Sent: Wednesday, December 26, 2007 9:45 AM
To: [email protected]
Subject: RE: res sidewall obstruction

We had Tyco run a test for NFPA 13 with residential sidewall installed
above cabinets mounted a 1' or so below. It was a fire on the counter
top and the cabinets were wrapped in craft paper to measure the water
droplet wetting.
The test failed, the cabinets shielded the fire. The sprinklers was not
able to extinguish the fire, it burnt out when the fuel ran out. Your
situations is a little different but it's food for thought. I have the
test on video, you might be able to get them to send you a copy if you
want.

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
www.burtellfire.com

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams
- FPDC
Sent: Wednesday, December 26, 2007 8:21 AM
To: [email protected]
Subject: res sidewall obstruction

I am working on a project where an old school is being converted to
Condos. The ceilings in the units are approximately 12 ft. The original
design called for sidewall sprinklers at about 11'-7". The owner has now
added closets that stick out into the room approx 2'-6". The top of the
closets are approx 8'-6". Do these closets now create an obstruction?
The requirements of 8.10.7.2.2 are met, but the diagram only shows a
wall.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to