I would go for a horizontal installation of you can.
Unless it's a poured concrete roof, I'd be wondering how to secure it well,
and they leak around the PIV, even with a sleeve.
You know they'll use it as a brace and subject to forces beyond the flowing
of water which will only make things worse.
Use a NRS gate and a wall post (I don't personally like Kennedy's wall post)
and lock or tamper it.
Not a huge increase in cost over the BV but I can understand the reasoning
of the AHJ.

Tom

See Croker 6641 or 6642, Potter Roemer 5850 or 5852 or other mfg.

Thom McMahon


I need to install standpipe hose valves on a roof top per NFPA 14 (07).
What I have done in the past is to provide a butterfly valve inside the
stairwell to control the roof valves but this particular AHJ is
requiring it to be installed per figure A7.3.2(d) with a non-rising stem
gate valve in the stairwell and some type of post indicator / capped
wrench head on the roof top to open the valve.  Any ideas on how to do
this without a major leak issue?  Also, what is the best way to secure a
PIV to a roof deck?
Thanks,
Dewayne