I've been traveling, so apologies for the late reply.   Dewayne, you
might remind the AHJ that the annex is suggested material and not
necessarily a "written-in-stone" mandate or prescription for the design
of a system or parts of one.   The sketch in A7.3.2(d) illustrates one
way of freeze protecting a roof manifold, but there are countless others
including the arrangement you describe.  The key feature of the
A7.3.2(d) sketch is that a firefighter can access the water supply
exclusively from the outside of the building; this means that you can
pipe to the roof manifold without consideration for access below, such
as running in a stairwell.  The valve could be concealed or in a chase
without leaving some other means of access for operating the valve.  If
the AHJ is satisfied with alternate means of access to the control
valve, there's no compelling reason to use a key valve as shown.

As far as anchoring a PIV - I'd get with the structural engineer.
Maybe a letter from him that you can't do it will motivate the AHJ to
relax his requirement.  Failing that, in my contracting years we always
coordinated with the contractor who was building the roof.  Show the
what you've got and how many actual membrane penetrations you have to
make for bolts, the operating stems (or the well for a wrench) and have
them come up with a method for water-proofing.  That part of it
shouldn't be a big deal.

Steve Leyton
Protection Design & Consulting

The foregoing is my opinion only and is not intended to represent the
Technical Committee on Standpipe Systems, nor serve as an interpretation
of NFPA 14.


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dewayne
Martinez
Sent: Friday, December 28, 2007 8:21 AM
To: [email protected]
Subject: Hose valves at roof top

I need to install standpipe hose valves on a roof top per NFPA 14 (07).
What I have done in the past is to provide a butterfly valve inside the
stairwell to control the roof valves but this particular AHJ is
requiring it to be installed per figure A7.3.2(d) with a non-rising stem
gate valve in the stairwell and some type of post indicator / capped
wrench head on the roof top to open the valve.  Any ideas on how to do
this without a major leak issue?  Also, what is the best way to secure a
PIV to a roof deck?  
Thanks,
Dewayne
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to