Hello Greg,
Looks like a check valve is needed in the leg of the tee that feeds
the standpipe and sprinkler. The FDC needs to be connected to that
legs also before that check valve. Otherwise it is a useless loop as
you suspect.
This is how I see your drawing, I condensed it a little to stop line
wrap.
Hydrants are "O" and fdc is "X"
STANDPIPE
I
I
"O" O" I
I---------I------I-------"X"----dcda-----SOURCE
"I" belive it should look like this:
Hydrants are "O" and fdc is "X"
^ is a check valve
STANDPIPE
I
I
"X" fdc
I
"O" O" "^" check valve
I---------I------I--------------dcda-----SOURCE
Thursday, January 10, 2008, 1:51:48 PM, you wrote:
> My picture did not work, sorry.
> Deal is this: Source to backflow with FDC, 6" continues to tee that feeds
> standpipe and sprinkler, from the tee 6" continues to 2 fire hydrants.
> When FD connects to hydrant they will connect back to fdc with the sprinkler
> main in between the 2. Will this create a useless loop or will it work?
> Thanks,
> Greg
> Living Water Fire Protection, LLC
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> Fax: 850-937-1852
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
> Sent: Thursday, January 10, 2008 9:09 AM
> To: [email protected]
> Subject: fdc loop
> We have a situation as follows:
>
> Hydrants are "O" and fdc is "X"
>
>
> STANDPIPE
> I
> I
> "O" "O" I
>
> I----------------------------I------I-------------------------"X"-dcda------
> ---SOURCE
>
> Question: Will this work or does it create a loop that will prevent the
> standpipe from receiving adequate pressure?
>
> Thanks,
> Greg
>
> Living Water Fire Protection
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> Fax: 850-937-1852
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
--
Best regards,
Charles mailto:[EMAIL PROTECTED]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)