The question that prompted the change was zackery this issue, ie the channels in the metal pan of a poured concrete floor assembly. Since the allowance to treat the panel pocket as obstructed construction and place the sprinklers further down from the ceiling is based on capturing heat, having all those open channels seemed counter- productive. Thus the clarification with the wording "including the interface at the roof". Granted the "roof" is on the outside but it's used synonymously with ceiling as in 3.9.16 Roof Height.

Roland

On Jan 17, 2008, at 11:53 AM, Steve Leyton wrote:

Per the above section, the definition panel construction was modified to include the language, " ... There should be no unfilled penetrations in
the cross sectional area of the  bounding structural members including
the interface at the roof."

Where structural steel decking is supported by steel beams and girders
that otherwise meet the definition of panel construction, was it the
committee's intent that the openings created by the decking flutes must be filled above the top chord of said beams and girders? Or does naked
steel decking still meet the intent of the definition of panel
construction?


Steve Leyton
PROTECTION DESIGN & CONSULTING
8849-B Complex Drive
San Diego, CA 92123
-------------------------------------------------------------
Ph:      858.751.2930 - Ext. 102
Fax:    858.751.2933
Cell:  619.972.5696


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:Sprinklerforum- [EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to