I already thought of that, but in the case I'm looking at now there
isn't any fire-proofing.  Maybe we could fill the voids with the broken
dreams of Patriot fans everywhere ...

Steve Leyton
Protection Design & Consulting


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Thursday, January 17, 2008 2:20 PM
To: [email protected]
Subject: Re: NFPA 13, 2002 A.3.7.1 (4)

We currently are doing a panel construction parking structure under a
mixed 
use building, and are relying on the fire proofing to fill those voids.
The spray on application generally does a pretty good job.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- 
From: "Roland Huggins" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Thursday, January 17, 2008 1:44 PM
Subject: Re: NFPA 13, 2002 A.3.7.1 (4)


> The question that prompted the change was zackery this issue, ie the 
> channels in the metal pan of a poured concrete floor assembly.  Since
the 
> allowance to treat the panel pocket as obstructed construction  and
place 
> the sprinklers further down from the ceiling is based on  capturing
heat, 
> having all those open channels seemed counter- productive. Thus the 
> clarification with the wording "including the  interface at the roof".

> Granted the "roof" is on the outside but  it's used synonymously with 
> ceiling as in 3.9.16 Roof Height.
>
> Roland
>
> On Jan 17, 2008, at 11:53 AM, Steve Leyton wrote:
>
>> Per the above section, the definition panel construction was
modified to
>> include the language, " ... There should be no unfilled  penetrations
in
>> the cross sectional area of the  bounding structural members
including
>> the interface at the roof."
>>
>> Where structural steel decking is supported by steel beams and
girders
>> that otherwise meet the definition of panel construction, was it the
>> committee's intent that the openings created by the decking flutes
must
>> be filled above the top chord of said beams and girders?  Or does
naked
>> steel decking still meet the intent of the definition of panel
>> construction?
>>
>>
>> Steve Leyton
>> PROTECTION DESIGN & CONSULTING
>> 8849-B Complex Drive
>> San Diego, CA 92123
>> -------------------------------------------------------------
>> Ph:      858.751.2930 - Ext. 102
>> Fax:    858.751.2933
>> Cell:  619.972.5696
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> To Unsubscribe, send an email to:Sprinklerforum- 
>> [EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to