Not as much now as they used to.
They can fail for a number of reasons but the majority fail due to lack of
flow and pressure from the FDV.  The pipe's too small, in a nutshell is the
case.
Our Building Code calls for these to deliver 500 GPM @ 100 PSI with flat 150
PSI at the FDC, and of course additional 250's for the others up to 1000 or
1250.
The inspectors will accept 155-160 PSI but that's it.  Most after failing
once, aside from the embarrassment, but with the failure causing no
occupancy and having to pay for an engine, 4 firefighters and an officer
plus to inspectors and maybe a cop; make sure it passes the second time (and
pay again) and most do.
They used to look at me cross-eyed when I'd ask if they hydraulically sized
the pipe but they're coming around and realizing it's an important
calculation to run.
I can go into how I do them if you want me to, but I think I've posted this
before.
I can write you of various systems that failed and the reasons and steps
taken to correct them, if you like.

What's interesting for me these days is the older systems.  I do a lot when
we were 65 PSI but I've also done some from the 70's when there wasn't a
number.
The client asks "Did we pass?", I turn to the inspector and ask the same and
he returns "You tell me.".  :P

Tom

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of R
Richardson
Sent: Tuesday, January 22, 2008 12:16 PM
To: [email protected]
Subject: RE: Testing of Dry Manual Standpipes


We too are evaluating the on-off enforcement of this requirement.

I would be very interested in your experience with these tests, do they fail
often and what is the source of failure?

Rich Richardson
Seattle Fire Department

>>> "Tom Duross" <[EMAIL PROTECTED]> 01/19/08 7:09 AM >>>
Every single standpipe installed in Boston gets tested.  If no pump, then an
engine and paid detail.
I do a lot of them with flowmeters and hose to the roof or down the stairs
to grade.
If it's below freezing and we can't get to a catchbasin and hydrant on the
same side of the street, it's scheduled for warmer weather and a condition
of acceptance.
If we have to cross a street for a hydrant or drain, they need a police
detail and temporarily shut down the street and/or redirect traffic and
people.

Tom


Our FD is more then glad to hook up an engine, handline and flow them.
(Except in the dead of winter)

Its a win-win-win, contractor gets it tested without having the greater
expense of renting his own equipment, AHJ gets his flow test and the FD gets
to work with the system and gain confidence in it.

John Drucker


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to