I agree Tom.  Here is what I plan to respond unless I hear words of wisdom from 
you guys.
   
   
  One must accept the fact that there are variables which affect the life of a 
sprinkler system.  They include:
   
  Proper original design and installation
  Proper inspection and testing
  Whether they are wet, dry, preaction or antifreeze
  Environmental conditions, like salt air, high humidity, corrosive atmosphere.
  Presence of microbiologically induced corrosion (MIC)
  Type of pipe, Schedule 40, thinner wall pipe, galvanized pipe, plastic pipe
  Corrosive nature of the water
  Earthquake
   
  A new or existing wet pipe system which has been tested free of the 
conditions leading to MIC, and is properly maintained, can pretty much be 
expected to last for the life of the building.  Examples of this are the 
sprinkler systems at The Presidio and Fort Mason in San Francisco.  I know the 
system at the Headquarters Building at Upper Fort Mason is in the neighborhood 
of 70 years old.  I took apart portions of another 70 year-old sprinkler system 
in San Francisco, during a building demolition.  The exterior and interior of 
the pipe was like brand new.
   
  Dry pipe systems do not have such a good history, mostly because of internal 
corrosion.  I know of no statistics, but would expect at 30 to 40 years.
   
  Antifreeze systems will not get proper maintenance, so it is anybody's guess.
   
  Other fire extinguishing systems will likely have shorter lives, partly due 
to obsolescence.

Tom Duross <[EMAIL PROTECTED]> wrote:
  That's kinda like asking how long is a piece of string Ed.

Tom
Go Pats

eBay


At 06:39 PM 1/25/2008, you wrote:

>Here is a question I was asked today:
> "Where can I find a list that indicates the Estimated Design life 
> for a fire
>suppression/sprinkler system?
>
> What say ye?
>
>
>Ed Vining


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)



Ed Vining
  4819 John Muir Rd
  Martinez CA 94553
  925-228-8792
  [EMAIL PROTECTED]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to