It would be at the discretion of whomever you are accountable to as far as submission of reports. If you submit reports to a local AHJ or Underwriter I would contact them and ask how stringently you need to follow the frequencies established in NFPA 25. I doubt that in a 365 day cycle a day or even a week would cause a collapse in the space-time continuum.
Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.lg.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] Sent: Tuesday, January 29, 2008 1:36 PM To: [email protected] Subject: grace period NFPA 25 establishes inspection, testing and maintenance frequencies. A grace period is not considered. Due to the large number and variety of fire systems throughout our site, these frequencies cannot be met on a rigid schedule. For example an Annual test is performed, does that mean the following year if the test is conducted on day 366 the test is delinquent? Is an impairment necessary? If an inspection is required monthly does that mean every 30 days? _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)