It would be at the discretion of whomever you are accountable to as far
as submission of reports.  If you submit reports to a local AHJ or
Underwriter I would contact them and ask how stringently you need to
follow the frequencies established in NFPA 25.  I doubt that in a 365
day cycle a day or even a week would cause a collapse in the space-time
continuum.  

Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Tuesday, January 29, 2008 1:36 PM
To: [email protected]
Subject: grace period

NFPA 25 establishes inspection, testing and maintenance frequencies. A
grace period is not considered. Due to the large number and variety of
fire systems throughout our site, these frequencies cannot be met on a
rigid schedule. 
For example an Annual test is performed, does that mean the following
year if the test is conducted on day 366 the test is delinquent?  Is an
impairment necessary?  If an inspection is required monthly does that
mean every 30 days? 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to