Geraldine, If I'm not mistaken isn't your email address the Savannah River Site and didn't you all just come out with some new guidelines for yourself? What does your AHJ say? And finally at least something to hang your hat on: Look in NFPA 25-1.3 & 1.3A-2007 ed. which allows alternatives. If you have the handbook better yet because it has a little more to say regarding leeway. Basically if your AHJ agrees that a few days off for monthlies or a week or two on annuals is OK as long as you regain that time so that a May inspection one year may be deferred until June the next but then occur in May the again the following year then that would be in keeping with intent. What you need to be cognizant of is not doing May this year, June the next and then July the next, thereby meeting the month (if given a month) leeway to the letter but missing the spirit and intent. This is akin to setting up a 13 month schedule. Such manipulation of largesse is why we end up with AHJs reading things of so literally.
On 1/29/08, [EMAIL PROTECTED] <[EMAIL PROTECTED]> wrote: > NFPA 25 establishes inspection, testing and maintenance frequencies. A > grace period is not considered. Due to the large number and variety of > fire systems throughout our site, these frequencies cannot be met on a > rigid schedule. > For example an Annual test is performed, does that mean the following year > if the test is conducted on day 366 the test is delinquent? Is an > impairment necessary? If an inspection is required monthly does that mean > every 30 days? > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)