This guidance is from the GSA PBS P100 criteria:

Track Files

General. A track file uses a single aisle to give access to an otherwise
solid group of open-shelf files. Access is gained by moving shelf units
on rollers along a track until the proper unit is exposed.
Special Requirements. Track files shall meet the following requirements:

1.  The track file system shall be constructed entirely of steel. At
least 1.4 mm (18-gauge) sheet metal shall be used for all parts of the
shelving unit.
2.  The system shall be no more than 2438 mm (8 feet) high, and a
minimum clearance of 457 mm (18 inches) shall be maintained between the
top of the shelving and the ceiling.
3.  The sprinkler density shall be 12.2 (L/min)/m2 (0.3 gpm/sq. ft.)
over 139 m2 (1500 sq.ft.). Sprinkler spacing shall be 9.3 m2 (100
sq.ft.) maximum.
4.  The back cover of stationary end files shall be solid sheet metal.

http://www.gsa.gov/gsa/cm_attachments/GSA_DOCUMENT/P100-2005_07_Fire_Life_Safety_R2-w-r-k_0Z5RDZ-i34K-pR.pdf

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.
372 Wilett Drive
Severna Park, MD 21146
410-544-3620 Phone
410-544-3032 FAX
412-400-6528 Cell

-------- Original Message --------
Subject: Re: High Density Shelving
From: Tom Wellen <[EMAIL PROTECTED]>
Date: Tue, January 29, 2008 9:28 am
To: [email protected]

What about the reference that can be found in the NFPA 13 Handbook
commentary in Section 8.14.9 in the 2002 ed. and 8.15.9 in the 2007 ed.?

Tom Wellen
AFSA Technical Services


On Jan 29, 2008, at 7:41 AM, Mike Hairfield wrote:

>
> Does anyone know how to protect a room with high density mobile
> shelving?
>
> There is a 2 foot clearance between the deflectors and top of the
> shelving.
>
> Mike Hairfield
> Nicholson Sprinkler Corporation
> ph 804-353-1822
> fax 804-358-9047
>
> Thanks!_______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:Sprinklerforum-
> [EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to