Mike 

You can find protection information on mobile shelving units in the following 
documents:

1.      Fire Protection Study, Mobile Compact Shelving Fire Tests, "Archives 
II", Gage-Babcock & Associates, Dated June 1990.

2.      Full Scale Fire Tests of Sprinklered Mobile Shelving Units for National 
Library of Canada, Gage-Babcock & Associates, Dated May 1992.

3.      Full-Scale Fire Tests and the Development of Design Criteria for 
Sprinkler Protection of Mobile Shelving Units, G.D. Lougheed, J.R. Mawhinney, 
and J. O'Neill, Fire Technology, First Quarter 1994, Volume 30, Number 1, 
pp.'s. 98 - 133.

If you client is an FM insured you should call the Local FM Field Engineer 
because FM has protection recommendations for this type of storage. 

Protection of these units is not just a "sprinkler" thing but involves building 
fire resistance rating of storage room and configuration of the mobile shelving 
units at rest or when parked.

Our recommendations to clients with this type of storage are as follows:

1.      Provide a mechanical means to maintain at all times a minimum 6-inch 
space between each shelving unit. 
2.      The compartment containing the rolling aisle storage shall be cut off 
from the remainder of the facility with two hour fire rated barrier (ceiling, 
floor and walls), with openings protected by 1½ hour, Class B, fire rated 
protective devices.
3.      Design the sprinkler system to provide a design density of 0.30 gpm per 
sq. ft. over the hydraulically most remote 3,000 sq. ft.
4.      Sprinkler head spacing shall not exceed 100 sq. ft. per head.
5.      The sprinklers shall be QR type, pendent style, ½ inch orifice, ½ inch 
NPT sprinklers, with a K factor of 5.6.

If the 6 inch space is not provided then the sprinkler system will not control 
the fire; protection for this type of storage is not just a "sprinkler" thing 
but is the synergy of spacing between the units, Fire resistive compartment 
containment and heavy sprinkler discharge density.   

Mike I hope this helps. 

Jim Davidson 
 
Davidson Associates 
302-378-7600
-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Mike Hairfield
Sent: Tuesday, January 29, 2008 8:45 AM
To: [email protected]
Subject: High Density Shelving


Does anyone know how to protect a room with high density mobile shelving?
 
There is a 2 foot clearance between the deflectors and top of the shelving.
 
Mike Hairfield
Nicholson Sprinkler Corporation
ph 804-353-1822
fax 804-358-9047
 
Thanks!_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to