Hello all,

To put fuel on a fire so to say....  The Electrician had disconnected
the air compressor on Friday for this dry system to install a proper
Disconnect (I raised hades about the "light Switch"). Well our crew
had left for the day and the electrician did not finish the disconnect.....

We had a 2" tri seal coupling that was installed wrong on a line feeding 4 
heads.

The air in the system leaked down, The system went wet, Leaked/Sprayed
water in a nice 1/8" stream onto the wall about 8" away, Water ran
down the wall, Through the Fire Panel that had been certified on
Thursday. Alas the panel was not monitored yet, Building was not
occupied yet, Alarm panel went into alarm until it drown, Then it went
into a "Release the electronic chip smoke" mode. I got a call on
Sunday from the GC that went down to do some paperwork the electrical
room was flooded. There had been about 900 gallons of water through
the meter on the back flow preventer since the alarm certification was
finished on Thursday. It was all "our" fault since we had a minor leak
in the system. Yes the Alarm company was a sub of the electrician.

Friday, February 1, 2008, 10:13:54 AM, you wrote:

> Just to add to the madness, we have a reviewer in Virginia asking for a
> second backflow at the riser inside the building per plumbing code. There is
> already one in the underground run-in right outside. No, there is no
> plumbing coming off of the run-in. How do you educate someone like this? It
> must be Friday!
> Chuck B

> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of George Church
> Sent: Friday, February 01, 2008 9:57 AM
> To: [email protected]
> Subject: RE: Funny - or not - inspection story.

> I think you only hydro High Voltage panels, not the typical low voltage used
> today. The high voltage can withstand the 200 psi; 270 PSI if it's a 220
> volt panel, 50 PSI over the normal working voltage.

> I don't blame you for not asking any questions.....but a high-pressure air
> test would be far safer, with permission of AHJ.

> glc

> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Dusha,
> Richard P. Mr.
> Sent: Friday, February 01, 2008 9:50 AM
> To: [email protected]
> Subject: RE: Funny - or not - inspection story.

> I've never heard of a hydrostatic test on a fire alarm panel. I'm thinking
> 200 psi of water pressure might damage the panel.

> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of douglas hicks
> Sent: Friday, February 01, 2008 9:43 AM
> To: [email protected]
> Subject: Re: Funny - or not - inspection story.

> Here is another inspection story.  I was waiting for an inspection on a UL
> 300 fire suppression system, and the inspector was late.  When he showed up,
> he was in a bad mood.  He had just been on a fire alarm test and the stupid
> contractor did not know how to  hydro  the fire alarm panel.  Luckily the
> building inspector know how to hydro the panel, or I would  not have had my
> inspection that day.   I was afraid to ask any questions.  That inspector
> was on a 30 day contract with the City until they hired another inspector.



> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

> To Unsubscribe, send an email
> to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)


-- 
Best regards,
 Charles                            mailto:[EMAIL PROTECTED]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to