Cliff, I gotta admit I've never heard a formal definition of what a communicating space is, but I've interpreted that to mean any adjacent room that heat from a fire could travel into and activate sprinklers. By calcing up to 2 sprinkles in each of these spaces, the sprinkler system shouldn't get overpowered.
I've been known to be wrong. Ed Kramer Littleton, CO > I understood the whole idea regarding communicating spaces was to escape > the > fire. Who is going to leave a larger office and hide in a closet to get > away from a fire? > > I guess I misunderstood the reasoning on this. > > Cliff > > -----Original Message----- > From: [EMAIL PROTECTED] > [mailto:[EMAIL PROTECTED] On Behalf Of Roland > Huggins > Sent: Tuesday, February 12, 2008 4:17 PM > To: [email protected] > Subject: Re: omitting closets in small building > > If you have an adjacent compartment with an unprotected opening, how > can you justify ignoring it just because it is small? > > Put a closer on the doors, then exclude them. > > Roland > > On Feb 12, 2008, at 1:01 PM, Cliff Whitfield wrote: > > > Todd, > > > > Could you not use the Room Design method for your calcs? That should > > eliminate the need to include those heads in the closets. I don't > > think a > > closet is considered a "communicating space" in this instance. > > > > Cliff _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)