What about applying area reduction? 

Brian Harris
FDFP INC.

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- FPDC
Sent: Tuesday, February 12, 2008 3:17 PM
To: [email protected]
Subject: omitting closets in small building

A 960 square foot (footprint) house is being converted to offices and a 13
system is to be installed. The top floor layout will not be changed and
there are several small closets, etc. which will require sprinklers. The
total number of sprinklers on that floor is 16. 
Section 14.4.4.4.2 allows for the sprinklers in the closets to be omitted if
the design area is as stated in section 11.2.3.1.5 (1500 sqft). Since the
building is smaller than the design area, would that require the sprinklers
in the closets to be included? Eliminating the closet sprinklers would cut
the number calculated in half.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080