I have had this happen before and it was due to sealing the head penetration. We drilled a 2" min. hole and sealed around the head with spray foam. That solved the problem.

Chris Payne
FPS

----- Original Message ----- From: "GAYLE KNOWLES" <[EMAIL PROTECTED]>
To: "sprinklerforum" <[email protected]>
Sent: Tuesday, February 19, 2008 2:29 PM
Subject: dry pendant in cooler



We have a situation with a dry pendant located minimum 24" away from coil in a cooler. Apparantly, condensation is building up on head and dripping water on cooler floor. This is a cooler box at a Walgreens. Box is very narrow and really no other place to put head. Has anyone experienced this before and come up with an idea to correct this problem? Walgreen's is telling us to put a baffle between head and coil. Not a good idea, altho, box is small enough that head will flood entire area, but baffle adds an obstruction. Thanks for any ideas or help. I actually told them, coil was running too cool. Go figure...I am not a refrigeration person.

Gayle Knowles, SET
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


--
No virus found in this incoming message.
Checked by AVG Free Edition.
Version: 7.5.516 / Virus Database: 269.20.8/1287 - Release Date: 2/19/2008 10:55 AM


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to