Could you foresee a fire senario where the 47 extra heads would operate.  I 
think that this is exactly what the exception is for.

Regards


----- Original Message -----
From: "Paul Pinigis" [EMAIL PROTECTED]
Sent: 22/02/2008 05:30 PM EST
To: <[email protected]>
Subject: RE: Gaggle of closets



Don't you just love it when the letter of the code works in your favor.
I really don't think that this is what the NFPA 13 committee had in mind
when they developed that section.

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Friday, February 22, 2008 5:05 PM
To: [email protected]
Subject: Gaggle of closets

I am looking an apartment building which is to be designed according
to NFPA 13. On the first level, there is a room which contains 55 -
3'x5' tenant storage closets (mostly filled with shelves). These
would need to be sprinklered, which is fine, but the issue comes in
the hydraulics. Section 14.4.4.4.2 states that closets with a single
sprinkler may be omitted from the calculation. There could be up to
47 closets in the remote area. I have used this exception numerous
times, but never in this quantity. The standard says nothing to the
contrary, so I could eliminate 47 sprinklers in the remote area
because they are in closets? Is there something I am overlooking?



Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


This document should only be read by those persons to whom it is addressed and 
is not intended to be relied upon by any person without subsequent written 
confirmation of its contents. Accordingly, our company disclaim all 
responsibility and accept no liability (including in negligence) for the 
consequences for any person acting, or refraining from acting, on such 
information prior to the receipt by those persons of subsequent written 
confirmation.

If you have received this e-mail message in error, please notify us immediately 
by telephone. Please also destroy and delete the message from your computer. 
The Unsolicited Electronic Message Act 2007 (The Spam Act) came into effect 
from 5 September 2007. As a valued client you may receive communications from 
us from time to time, including electronic publications, invitations and 
related information. Please advise if you wish us to stop sending these 
communications to you. Otherwise we will assume you wish to continue receiving 
these communications from us. 

Any form of reproduction, dissemination, copying, disclosure, modification, 
distribution and/or publication of this e-mail message is strictly prohibited.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to