Attics in 13D systems don't require sprinklers. 8.6.5 (2002)

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
 
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
Sent: Tuesday, February 26, 2008 1:16 PM
To: [email protected]
Subject: 2nd request 13d attic storage

Doesn't anyone have something to say?

We are beginning to see more 13d installations here and I know some of you
disagree but one of the local AHJ's only require 13d systems in townhomes.

Some of these buildings are being framed and decked for small storage areas
in the attics much like most of us have in our own homes.These areas
typically do not have enclosed walls and ceiling is the sloped roof deck.

How are you AHJ's handling this? Are you just placing heads above the
storage deck or are you requiring the areas to be enclosed as a room? 

The challenge is obviously freeze protection. In a room that is heated there
is no problem except the local AHJ then interprets the room as another floor
which cause other building code issues.

Any experiences \ ideas?

Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to