Treat it as if there was a soffit ?
Over 8" wide, you sprinkler below it.
SSp would cover the blocked area of HSW spray.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
Sent: Tuesday, February 26, 2008 8:21 AM
To: [email protected]
Subject: RE: obstructions below sidewalls

We had the same situation in a condo and contacted the sprinkler
manufacturer. In our case we put heads under the light cove to cover the
"shadow" and the sidewall protected the center of the room. This was
approved by the manufacturer as far as their input goes. The AHJ also
accepted this.

Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams
- FPDC
Sent: Tuesday, February 26, 2008 7:01 AM
To: [email protected]
Subject: obstructions below sidewalls

I have run into a couple of situations lately where there have been 
continuous obstructions directly below sidewall sprinklers that 
extend from the wall the sidewall is fed from. The latest is a light 
cove that sticks out 11" from the wall and is 8" below the sprinkler. 
I can't find anything in 13 that discusses or would relate to this. 
Most of the discussion in 8.7.5.2.1 related to "dry shadow" in front 
of and not underneath. Am I missing something? Any thoughts?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to