The exception says that sprinklers may be excepted where there is no "... storage or handling of combustibles." You may not have storage, but you sure do have handling. I believe the wording of the exception was very carefully chosen so that loading dock overhangs would still require sprinklers.
Steve Leyton Protection Design & Consulting -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan Sent: Monday, March 10, 2008 1:04 PM To: [email protected] Subject: non-combustible overhangs I am just checking myself here; but if you have a non-combustible overhang over 4' wide (actually about 6')under which 18 wheelers back up and unload, are sprinklers required? These are box trucks and they carry carpet. The carpets are really never exposed as they go straight from truck to warehouse. What say ye learned ones? Thank you, Greg McGahan Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)