Greg, you are not the least of the regular contributors. We all have something to bring to the table and it all has value to someone.

This is really turning into a multi-faceted discussion. First, there is an assumption that at some point in the immediate future, there is going to be a need for a b'zillion 13D systems all at once. I don't see that. With the housing market the way it is right now and the median price of a home dropping almost $40,000 in the last two years (heard that this morning - $231K down to $193K), no legislative entity is going to add something that will increase home prices, especially retroactively, until this gets sorted out. Even if NFPA or IBC includes something, it will take several Code revision cycles to implement this and there are always the possibility of exclusions. There may end up being some up-tick larger developments, but I don't see a big flood of new systems coming right away.

As far as plumbers doing 13D systems, there may be some, but I don't think that every guy with a wrench and a pick-up truck is going to start doing them. Once they see the design and review process, many will opt out. The liability issue hasn't even been discussed yet, but that will have an impact. Where the burden will fall is on the AHJ to review and determine if the system is being done properly. Most are over-worked and under-staffed now.

Now to designers. Most all of the designers that I know learned their craft working through their employer. Seneca has a school for design and there may be one or two others, but still most of us learned on-the-job. I think it will take establishing design programs through trade schools or community colleges before you actually start pumping out designers in significant numbers. Set up co-op programs with local contractors to get some reality based education included and I think we would be on to something. Hey, sometimes I wouldn't mind getting out of the rat race and spend my last 15 years teaching.

Fodder for thought. I'm sure someone will have a comment.


At 09:23 AM 3/25/2008, you wrote:
I said "still" - meaning we already have non-compliant work being performed.
I am not casting stones at them without casting it at myself first.

If the plumbers or welders or sheetrock finisher's or any other trade could
step in and fix our design and labor shortage; they will then become part of
our industry and we will learn from them or be pushed out. I consider myself
the least of the regular contributors to this forum and I think I am
reasonably intelligent. I have beat my head and chest to find a solution to
the design problem in my own little world with poor results. I am sure the
smarter and more experienced among us have tried even harder and the results
have obviously been the same for the industry as a whole.

It is not a stretch to say that if another trade can fix our industries'
problems then I personally embrace the help and hope I am wise enough to
learn what they know and implement it in my life.

Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of George Church
Sent: Tuesday, March 25, 2008 8:00 AM
To: [email protected]
Subject: RE: Fire Systems and Plumbers

Greg, there are enough terrible jobs being done by our own industry that we
should refrain from throwing rocks at mechanicals/plumbers.

I'm sure, like me, you try very hard to toe the line in your sphere of
control, but alas, there are plenty of non-compliant jobs being installed by
sprinkies that are either ignorant or relying on "but that's what was
specified" if not out-and-out greed.

Seriously, how many 30' tall spec/flex buildings are protected to OH2 by
sprinkler guys?

I'm not saying plumbers are the answer, or that they do better or worse than
sprinkler contractors. The reality is we've abandoned the market segment by
never showing up in force.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
Sent: Tuesday, March 25, 2008 8:46 AM
To: [email protected]
Subject: RE: Fire Systems and Plumbers

Ok, so their pond has better candidates for designers than our pond which is
the USA? No, they will have unqualified people designing and you are still
going to have AHJ's that do not know the code letting them get away with
inadequate work.

I am sorry but I do not know the answer but bringing in another trade will
get more work done, but not done better.

Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Bill Minkel
Sent: Tuesday, March 25, 2008 7:25 AM
To: [email protected]
Subject: RE: Fire Systems and Plumbers

 I think the mechanical contractors are fishing in a way bigger pond than
the sprinkler contractors are.


Bill Minkel, Designer
Western States Fire Protection, Dallas
NFPA Member #2578666

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan
Sent: Tuesday, March 25, 2008 6:58 AM
To: [email protected]
Subject: RE: Fire Systems and Plumbers

OK, so the plumbers are going to "miraculously" do what the sprinkler
industry can't and immediately discover qualified designers behind the rocks
OR they are going to be able to train them effectively when we can not?

I am crying foul here - I don't care what code you are using D, R or full
13, the issue is the same. I know we have spent money and time trying to
train and I am sure you more experienced guys have spent exponentially more
than us "young" guys. The problem is deeper - MANY Americans do not want to
work in ANY field and they definitely REFUSE to take responsibility for
their own lives and careers.

Bring me a person of character and integrity and I can train them and they
will work if they have basic natural ability. I have seen many, dozens of
people with the natural ability fail repeatedly due to character and
integrity issues.

I am sure the plumbers will take and perform the work; but I am even more
certain that they will have the same problems we already do to a much larger
degree and with less accountability.

Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Vining
Sent: Tuesday, March 25, 2008 12:58 AM
To: [email protected]
Subject: Re: Fire Systems and Plumbers

Not quite.  The NEC has the requirements for wiring of fire alarm systems,
but NFPA 72 (laughingly called the National Fire Alarm Code) stands on its
own.

On Mon, Mar 24, 2008 at 8:56 PM, Timothy W Goins <[EMAIL PROTECTED]> wrote:
> Big difference, NFPA 72 is part of the electrical code, or it was the
> last  time I checked.
>
>
>  -----Original Message-----
>  From: [EMAIL PROTECTED]
>
>
> [mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
>  Sent: Monday, March 24, 2008 8:43 PM
>  To: [email protected]
>  Subject: RE: Fire Systems and Plumbers
>
>
>
>  No different then Electrical Contractors that install Line Voltage
> Interconnected Smoke/Carbon Monoxide Alarms in Homes versus Alarm
> contractors that install Low Voltage Fire Alarm Systems.
>
>  Bottom line its about cost. The plumbing contractor who installs
sprinklers
>  as an extension of the plumbing system is no different then the
electrical
>  contractor who installs smoke alarms as an extension of the
> electrical  system.
>
>  As for the NFPA, do they really "represent" any particular trade or
merely
>  fire safety interests as a whole ?
>
>  John Drucker
>  Fire Protection Subcode Official (AHJ)  New Jersey
>
>
>
>  -----Original Message-----
>  From: [EMAIL PROTECTED]
>  [mailto:[EMAIL PROTECTED] On Behalf Of Steve
Leyton
>  Sent: Monday, March 24, 2008 7:13 PM
>  To: [email protected]
>  Subject: RE: Fire Systems and Plumbers
>
>  Booyah!  Well put, oh great poobah of sprinkie-stuff.  This is the dirty
>  little secret (or 600-lb. gorilla in the living room, depending on your
>  perspective) that I was alluding to in my rant a few weeks back about
>  large plumbing contractors moving into residential sprinklers.   Unless
>  we (WE, the fire sprinkler community, inclusive) seriously ramp up our
human
>  and training resources for designers and installers, it will be
impossible
>  to deal with the flood of proposal requests that are
>  inevitable.   This has been recognized and in some cases is already
>  being acted upon by certain plumbing firms on a regional basis.
>
>  Back to Timothy's question (aren't you glad you opened THIS can of worms
>  Tim-bo?); presuming it was a Uponor system you saw advertised, keep in
>  mind that they're market-making right now.   And the NFPA Journal is one
>  of several publications in which they're advertising, along with Rehau
who
>  manufactures the only other PEX product approved for 13D systems at the
>  moment.  If you don't want to see fire protection ads directed at
plumbers,
>  then you'll also definitely want to avoid PM Engineer and Contractor
>  magazine too.
>
>  Steve Leyton
>  Protection Design & Consulting
>
>
>  -----Original Message-----
>  From: [EMAIL PROTECTED]
>  [mailto:[EMAIL PROTECTED] On Behalf Of Steve
Muncy
>  Sent: Monday, March 24, 2008 3:01 PM
>  To: [email protected]
>  Subject: Re: Fire Systems and Plumbers
>
>  For multi-systems, there are currently several states that REQUIRE
>  that a licensed plumber install the system because they are considered
>  an extension of the domestic water supply.  Fire sprinkler contractors
>  are PROHIBITED from installing such systems, unless of  course they
>  have a plumbing license -- but the system is still being installed
>  under the plumbing license.  And when those systems are inspected,
>  they will be inspected by Plumbing officials - not the fire marshal.
>
>  Multi-purpose systems have  been been recognized as acceptable in
>  NFPA-13D for a long time but it was not until fairly recently that use
>  use accelerated.  New changes being incorporated into the
>  International Plumbing Code offer a simplified design for multi-
>  purpose systems that does not require hydraulic calcs but is based on
>  distance and water pressure. My understanding is that the NFPA-13D
>  committee has accepted the language proposed in the IPC proposal.  By
>  the way, it was the International Association of Fire Chiefs who
>  recommended the code change to add the simplified procedure to the IPC.
>
>  Bottom line is that you are going to see a lot more of these systems
>  in the future.  It is likely that most "lower-end" homes will adopt
>  the multi-purpose approach and larger, more expensive homes will have
>  a standalone system.
>
>  When (not IF) the International Residential Code moves the
>  requirements for sprinklers in single-family dwellings from the
>  appendix to the body of the code, thus making it required, the number
>  of residential systems will EXPLODE. Sure, there will be battles on
>  the local level to remove that requirement, but it is more difficult
>  to remove a provision from the code on a local level.
>
>  Think about this - based on the number of new homes built in 2007,
>  each and every fire sprinkler contractor in the country would have to
>  install 375 single-family fire sprinkler systems.  That is how big
>  this market will eventually be, and most fire sprinkler contractors
>  don't do many single-family systems when there are plenty of more
>  lucrative commercial jobs to dedicate the limited number of employees
>  to.
>
>  If plumbers are going to do this work.... and they will.... let's just
>  hope that they feel the need to acquire some TRAINING on the subject
>  before they jump head-first into the fire protection business.
>
>
>
>
>  Steve Muncy, CAE                         Fire Sprinklers Save Lives!
>  American Fire Sprinkler Assn.
>  Dallas, TX
>
>
>
>  On Mar 24, 2008, at 9:58 AM, Timothy W Goins wrote:
>  > Why would the NFPA journal, MAR/APR 2008 edition, use an advertiser
>  > for
>  > residential piping systems that ONLY recommends plumbers to install
>  > their
>  > product? I know the answer is money, but I thought they were looking
>  > out for
>  > our industry and it's standards, both written and installed.
>  >
>  > Isn't this like having an architect layout "design" fire sprinkler
>  > systems?
>
>
>
>
>
>
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>
>
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>



--
Ed Vining
4819 John Muir Rd
Martinez CA 94553
925-228-879
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080 _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to