As long as the area of the small room in question divided by the number of sprinklers in the room averages less than 225 square ft per sprinkler, the 9ft rule supercedes the S x L area calculation. It is my understanding this allowance applies whether there is one sprinkler or more in the small room since a small room, by definition, can be up to 800 sq.ft. in area, thereby requiring more than one sprinkler to protect it.
However, the 9ft allowance from a wall for a sprinkler or row of sprinklers can only be applied off of ONE wall in the small room. The reasoning is to allow for greater spacing in this one particular instance to account for lights, hvac, or other ceiling obstructions in an area than would otherwise be properly protected by the S x L spacing requirements and is only allowed in areas of light-hazard claassification. This is an allowance from the NFPA committee to keep the costs of installation automatic sprinklers at a reasonable level (without jeopardizing life safety) in these lower-hazard areas. Ray Vance Chief Engineering Tech. Wayne Automatic Fire Sprinklers, Inc. www.warp-drive.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris Sent: Wednesday, April 02, 2008 11:03 AM To: [email protected] Subject: Small Room Rule Forum, I trip myself every time I come across the "Small Room Rule", A.8.6.3.2.4(c) 07' edition. Isn't the head that is 9'-0" off the wall "covering" 270 sq.ft.? Regards, <http://www.firstdefensefire.com/> E-mail message checked by Spyware Doctor (5.5.0.178) Database version: 5.09530 http://www.pctools.com/spyware-doctor/ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)