Sorry Ken, my fingers are sometimes faster than my brain. Ed
> -----Original Message----- > From: [EMAIL PROTECTED] [mailto:sprinklerforum- > [EMAIL PROTECTED] On Behalf Of Ed Kramer > Sent: Wednesday, April 02, 2008 11:55 AM > To: [email protected] > Subject: RE: Small Room Rule > > Ray, > > Why does the sprinkler need to be farther than 7'-6" from a wall to > apply > 8.6.2.1.2? I interpret it that as long as the room meets the definition > of > 'small room', the area of coverage and min flow (in your example) will > be > 156 sf and 15.6 gpm. Maybe the wording was somewhat different in > previous > editions of 13. > > Ed Kramer > Littleton, CO > > > -----Original Message----- > > From: [EMAIL PROTECTED] [mailto:sprinklerforum- > > [EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED] > > Sent: Wednesday, April 02, 2008 11:03 AM > > To: [email protected] > > Subject: Re: Small Room Rule > > > > Ed, > > > > I respectfully disagree. In a 13' x 12' (156 sqft) room protected by > a > > single sprinkler, with the East-West spacing to the walls at 7-'6" and > > 5'-6, respectively, and the North-South spacing at 7'-6" x 4'-6" > > respectively, the area of coverage for the sprinkler is indeed 225 > > square feet, by use of the SxL=A method from NFPA-13. The required > flow > > from that sprinkler would be 22.5 gpm, based on light hazard density. > > > > However, if either (not both) the North-South or East-West dimensions > > were shifted so that the sprinkler is spaced greater than 7'-6" off of > > one (only one) wall, the protection area of coverage for the sprinkler > > as defined in 8.6.2.1.2 becomes 156 square feet, and the demand is > > reduced down to 15.6 gpm, based on the square footage of the room > > divided by the number of sprinklers in the room, and again a light > > hazard density. > > > > That's an old sprinkler designers tool, taught to me by an old > sprinkler > > designer tool, which was the kindest of names I eventually came to > call > > him. > > PARSLEY CONSULTING > > Ken Wagoner, SET > > 760.745.6181 voice > > 760.745.0537 fax > > [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail > > www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website > > > > > > > > Ed Kramer wrote: > > > Brain, > > > > > > In 'small rooms', section 8.6.2.1.2 applies. Area of coverage is > 225 > > sf. > > > > > > Ed Kramer > > > Littleton, CO > > > > > > > > > > > > > > >> Forum, > > >> I trip myself every time I come across the "Small Room Rule", > > >> A.8.6.3.2.4(c) 07' edition. Isn't the head that is 9'-0" off the > wall > > >> "covering" 270 sq.ft.? > > >> > > >> > > >> Regards, > > >> > > >> > > >> <http://www.firstdefensefire.com/> > > >> > > > > > > _______________________________________________ > > > Sprinklerforum mailing list > > > [email protected] > > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > > > To Unsubscribe, send an email to:Sprinklerforum- > > [EMAIL PROTECTED] > > > (Put the word unsubscribe in the subject field) > > > > > > > > > > > _______________________________________________ > > Sprinklerforum mailing list > > [email protected] > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > To Unsubscribe, send an email to:Sprinklerforum- > > [EMAIL PROTECTED] > > (Put the word unsubscribe in the subject field) > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:Sprinklerforum- > [EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)