Sorry Ken, my fingers are sometimes faster than my brain.

Ed

> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:sprinklerforum-
> [EMAIL PROTECTED] On Behalf Of Ed Kramer
> Sent: Wednesday, April 02, 2008 11:55 AM
> To: [email protected]
> Subject: RE: Small Room Rule
> 
> Ray,
> 
> Why does the sprinkler need to be farther than 7'-6" from a wall to
> apply
> 8.6.2.1.2?  I interpret it that as long as the room meets the definition
> of
> 'small room', the area of coverage and min flow (in your example) will
> be
> 156 sf and 15.6 gpm.  Maybe the wording was somewhat different in
> previous
> editions of 13.
> 
> Ed Kramer
> Littleton, CO
> 
> > -----Original Message-----
> > From: [EMAIL PROTECTED] [mailto:sprinklerforum-
> > [EMAIL PROTECTED] On Behalf Of [EMAIL PROTECTED]
> > Sent: Wednesday, April 02, 2008 11:03 AM
> > To: [email protected]
> > Subject: Re: Small Room Rule
> >
> > Ed,
> >
> > I respectfully disagree.  In a 13' x 12' (156 sqft) room protected by
> a
> > single sprinkler, with the East-West spacing to the walls at 7-'6" and
> > 5'-6, respectively, and the North-South spacing at 7'-6" x 4'-6"
> > respectively, the area of coverage for the sprinkler is indeed 225
> > square feet, by use of the SxL=A method from NFPA-13.  The required
> flow
> > from that sprinkler would be 22.5 gpm, based on light hazard density.
> >
> > However, if either (not both) the North-South or East-West dimensions
> > were shifted so that the sprinkler is spaced greater than 7'-6" off of
> > one (only one) wall, the protection area of coverage for the sprinkler
> > as defined in 8.6.2.1.2 becomes 156 square feet, and the demand is
> > reduced down to 15.6 gpm, based on the square footage of the room
> > divided by the number of sprinklers in the room, and again a light
> > hazard density.
> >
> > That's an old sprinkler designers tool, taught to me by an old
> sprinkler
> > designer tool, which was the kindest of names I eventually came to
> call
> > him.
> > PARSLEY CONSULTING
> > Ken Wagoner, SET
> > 760.745.6181 voice
> > 760.745.0537 fax
> > [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
> > www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
> >
> >
> >
> > Ed Kramer wrote:
> > > Brain,
> > >
> > > In 'small rooms', section 8.6.2.1.2 applies.  Area of coverage is
> 225
> > sf.
> > >
> > > Ed Kramer
> > > Littleton, CO
> > >
> > >
> > >
> > >
> > >> Forum,
> > >> I trip myself every time I come across the "Small Room Rule",
> > >> A.8.6.3.2.4(c) 07' edition. Isn't the head that is 9'-0" off the
> wall
> > >> "covering" 270 sq.ft.?
> > >>
> > >>
> > >> Regards,
> > >>
> > >>
> > >> <http://www.firstdefensefire.com/>
> > >>
> > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > [email protected]
> > > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > > To Unsubscribe, send an email to:Sprinklerforum-
> > [EMAIL PROTECTED]
> > > (Put the word unsubscribe in the subject field)
> > >
> > >
> > >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > To Unsubscribe, send an email to:Sprinklerforum-
> > [EMAIL PROTECTED]
> > (Put the word unsubscribe in the subject field)
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> To Unsubscribe, send an email to:Sprinklerforum-
> [EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to