Travis,
You'll have to look at the concealed space requirements in NFPA 13
and see if it conforms. I believe that the insulation exception is a
special case because it is not a hard, fixed surface. I've had to do
under catwalks in the past, so you might.
My brain cooked about noon today.
Todd
At 06:07 PM 4/4/2008, you wrote:
I am working on a project where there is a decent sized attic (21' above the
ceiling at the peak). The drop ceiling is 2' below the bottom of the
trusses. I have sprinklers at the roof deck and in the ceiling. However,
there is a walkable plywood deck placed on the bottom chord throughout a
large portion of this attic. Will I need to add another level of sprinklers
in the space between the walkable plywood and the ceiling? I know you don't
have to add sprinklers in the "interstitial" space between insulation placed
between joists and the ceiling if you have sprinklers at the roof deck.
But, I don't know if this would be a similar scenario to allow for the
sprinklers to be left out. I am brain dead on a Friday and not sure today.
Thanks in advance for your help!
Travis
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)