First, do you have insulation between the joists? From your post you seem to imply this is the case but if I read it another way it seems you don't since you have a catwalk of sorts. If the insulation is there then I'd presume the catwalk to be above it or it's for the interstitial dwelling gnomes. If it's above it it's protected by the roofline sprinklers. If it's below it you're working for some weird dudes. Is it less than four feet wide? I doubt if that rule applies where the insulation is between joists and presumably filling the space below the catwalk. I see the drop ceiling, the interstitial space, the insulation filling the voids both horizontally and vertically between joists then 4x8 sheets of plywood running the length of the attic through the center, a prismatic void space, rows of sprinklers, rafters and decking. If so I think you're OK. Move the insulation to the rafters and you'll need to sprinkler under the plywood or shave it down to 47 7/8" x 96".
On Fri, Apr 4, 2008 at 3:07 PM, Travis Mack, SET <[EMAIL PROTECTED]> wrote: > I am working on a project where there is a decent sized attic (21' above the > ceiling at the peak). The drop ceiling is 2' below the bottom of the > trusses. I have sprinklers at the roof deck and in the ceiling. However, > there is a walkable plywood deck placed on the bottom chord throughout a > large portion of this attic. Will I need to add another level of sprinklers > in the space between the walkable plywood and the ceiling? I know you don't > have to add sprinklers in the "interstitial" space between insulation placed > between joists and the ceiling if you have sprinklers at the roof deck. > But, I don't know if this would be a similar scenario to allow for the > sprinklers to be left out. I am brain dead on a Friday and not sure today. > > Thanks in advance for your help! > > Travis > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:[EMAIL PROTECTED] > (Put the word unsubscribe in the subject field) > -- Ron Greenman at home.... _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)