As far as I know the only time you need specifically listed concealed space sprinklers is when you're protecting plastic pipe in combustible spaces with sprinklers attached to the plastic pipe. Since I'd only be using dry heads in unheated spaces I'd presume a dry system which you can't use for dry systems or coming from pipe in a heated space to protect an unheated space so no plastic to protect. Educate me if I'm missing something.

On Apr 8, 2008, at 9:17 AM, Todd Williams - FPDC wrote:

True, but if the space requires sprinklers listed for concealed spaces per 8.14.1.6, then what are we supposed to do?


At 11:36 AM 4/8/2008, you wrote:
Todd,

Tyco, and probably others, make dry uprights up to four feet long.

On Tue, Apr 8, 2008 at 7:32 AM, Todd Williams - FPDC <[EMAIL PROTECTED]> wrote:
> Is anybody making or planning to make a dry upright concealed space
> sprinkler? I could use about 20 next week.
>
>  Todd G. Williams, PE
>  Fire Protection Design/Consulting
>  Stonington, Connecticut
>  www.fpdc.com
>  860.535.2080  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
www.fpdc.com
860.535.2080  _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Ron Greenman
...at home





_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to