Which ALSO requires modification to the joist space in most cases I have
seen.

Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Tuesday, April 08, 2008 12:04 PM
To: [email protected]
Subject: Re: dry concealed space sprinklers

A concealed space with a height less than 36 inches (as well as a few  
other parameters such as a combustible upper surface) requires a  
specific listing for concealed spaces (13:8.15.1.6 07 edition).

Roland

On Apr 8, 2008, at 9:27 AM, Ron Greenman wrote:

> As far as I know the only time you need specifically listed  
> concealed space sprinklers is when you're protecting plastic pipe  
> in combustible spaces with sprinklers attached to the plastic pipe.  
> Since I'd only be using dry heads in unheated spaces I'd presume a  
> dry system which you can't use for dry systems or coming from pipe  
> in a heated space to protect an unheated space so no plastic to  
> protect. Educate me if I'm missing something.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to