Which ALSO requires modification to the joist space in most cases I have seen.
Thank you, Greg McGahan Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Roland Huggins Sent: Tuesday, April 08, 2008 12:04 PM To: [email protected] Subject: Re: dry concealed space sprinklers A concealed space with a height less than 36 inches (as well as a few other parameters such as a combustible upper surface) requires a specific listing for concealed spaces (13:8.15.1.6 07 edition). Roland On Apr 8, 2008, at 9:27 AM, Ron Greenman wrote: > As far as I know the only time you need specifically listed > concealed space sprinklers is when you're protecting plastic pipe > in combustible spaces with sprinklers attached to the plastic pipe. > Since I'd only be using dry heads in unheated spaces I'd presume a > dry system which you can't use for dry systems or coming from pipe > in a heated space to protect an unheated space so no plastic to > protect. Educate me if I'm missing something. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)