I would think no on the sprinkler. Do you have an outside wall with the cooler not opening into the building but rather to the atmosphere? In other words, do you have to walk outside to get to the cooler? If I have pictured this correct I don't think you have to protect it. The only thing that comes to the top of my mind is that maybe you can't consider it independent because of lack of separation.
Rod DiBona Vice President Rapid Fire Protection [EMAIL PROTECTED] 605-348-2342 ph 605-391-3553 cell -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - FPDC Sent: Tuesday, April 08, 2008 2:46 PM To: [email protected] Subject: cooler A cooler outside the building envelope, but opens into the space. Sprinkler or no? If yes, would a dry sidewall into the cooler be acceptable? Otherwise you would have to run an anti-freeze or small dry system with pipe outside the building. Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut www.fpdc.com 860.535.2080 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)