I would think no on the sprinkler. Do you have an outside wall with the
cooler not opening into the building but rather to the atmosphere? In
other words, do you have to walk outside to get to the cooler? If I have
pictured this correct I don't think you have to protect it. The only
thing that comes to the top of my mind is that maybe you can't consider
it independent because of lack of separation.  


Rod DiBona
Vice President
Rapid Fire Protection
[EMAIL PROTECTED]
605-348-2342 ph
605-391-3553 cell

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - FPDC
Sent: Tuesday, April 08, 2008 2:46 PM
To: [email protected]
Subject: cooler

A cooler outside the building envelope, but opens into the space. 
Sprinkler or no? If yes, would a dry sidewall into the cooler be
acceptable? Otherwise you would have to run an anti-freeze or small dry
system with pipe outside the building.

Todd G. Williams, PE
Fire Protection Design/Consulting