Depends on the size of the cooler.  I did a Pizza Restaurant and had the
same deal, cooler was outside the building but had a door with direct
access to the kitchen.  We were able to use a dry sidewall from the
kitchen side to cover it.  Hopefully you don't have any obstruction
issues with the overhead refrigeration condensing coils or units.  In
some of the coolers they can be in the way and cause obstruction
problems. But if it is too deep to use a sidewall or it would be
obstructed then you may have to run a small anti-freeze system if that's
acceptable to your AHJ.  Seems overkill to have to go to all the trouble
to go with a dry system for just what will likely be only a couple of
heads.


Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 


On Apr 8, 2008, at 1:46 PM, Todd Williams - FPDC wrote:

> A cooler outside the building envelope, but opens into the space.  
> Sprinkler or no? If yes, would a dry sidewall into the cooler be 
> acceptable? Otherwise you would have to run an anti-freeze or small 
> dry system with pipe outside the building.
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080  _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:Sprinklerforum- 
> [EMAIL PROTECTED] (Put the word unsubscribe in the subject 
> field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to