Depends on the size of the cooler. I did a Pizza Restaurant and had the same deal, cooler was outside the building but had a door with direct access to the kitchen. We were able to use a dry sidewall from the kitchen side to cover it. Hopefully you don't have any obstruction issues with the overhead refrigeration condensing coils or units. In some of the coolers they can be in the way and cause obstruction problems. But if it is too deep to use a sidewall or it would be obstructed then you may have to run a small anti-freeze system if that's acceptable to your AHJ. Seems overkill to have to go to all the trouble to go with a dry system for just what will likely be only a couple of heads.
Craig L. Prahl, CET Fire Protection Group Mechanical Department CH2MHILL Lockwood Greene 1500 International Drive PO Box 491, Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 [EMAIL PROTECTED] http://www.ch2m.com On Apr 8, 2008, at 1:46 PM, Todd Williams - FPDC wrote: > A cooler outside the building envelope, but opens into the space. > Sprinkler or no? If yes, would a dry sidewall into the cooler be > acceptable? Otherwise you would have to run an anti-freeze or small > dry system with pipe outside the building. > > Todd G. Williams, PE > Fire Protection Design/Consulting > Stonington, Connecticut > www.fpdc.com > 860.535.2080 _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum > > To Unsubscribe, send an email to:Sprinklerforum- > [EMAIL PROTECTED] (Put the word unsubscribe in the subject > field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)