Agree - Jockey pumps or Pressure maintenance pumps as the standard calls them, do not have to be listed.
Hope this helps, John John August Denhardt, P.E. Strickland Fire Protection Incorporated 5113 Berwyn Road College Park, Maryland 20740 Office Telephone Number: 301-474-1136 Mobile Telephone Number: 301-343-1457 FIRE SPRINKLERS SAVE LIVES -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Roland Huggins Sent: Wednesday, April 16, 2008 12:56 PM To: sprinklerforum@firesprinkler.org Subject: Re: Help with jockey pump listing this section is addressing the use of other types of FIRE pumps. The standard does not identify types of Jockey pumps that you can deviate from. They are not required to be listed. This will be better clarified in the next edition (based on the outcome of the recent ROP) Roland On Apr 16, 2008, at 6:29 AM, Rod DiBona wrote: > When I look at NFPA #20 section 5.1.2.1 it looks like a jockey pump > must > be listed. I had it in my mind that it didn't. My mind vs the > standard? > ...probably not a fair contest but just wanted to check and see if > I am > missing something. Thanks. > > Rod DiBona > Vice President > _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)